Here is a link of the circuits I have
here. I can't tell if it is a 15A or a 20A. And thank you for the link. If it all works out, then I just need to replace the standard wall socket with one that accepts a 5-20, correct?
Looks like you're wired for 20A - you should have NEMA 5-20 outlets already. No, you cannot simply swap a 5-15 for a 5-20... the breakers and wiring have to handle the increased current, too. While I don't think a 5-20 on a 15A circuit is against code, you still wouldn't get more than 15A out of it.
Here is a link to verify this unit's input
here. Just to make sure by you.
Don't go by that - 80 Plus isn't really a safety certification company. Look on the label of the unit itself. If it's good to 100-120VAC, it will tell you there. You can't always trust labels, especially with the gutless wonders, but SF is a good company. If
it says 200-240, be ready to spend money on installing a proper 240V circuit just for that unit. In that case, it either wouldn't run at the lower voltage, may run to a point, or simply go pop.
This particular model isn't available in North America because 15A household circuits cannot run it to full power. However, a 20A circuit should be able to at least get close. I've thought about getting these for my mining computers, as they all run at 240V, but it's not worth it for me as they all run just fine off 1250-1600W units. Including two of the Super Flower 1600W monsters.
Why do you need this thing, anyway? I've got 7 video cards cranking on one of those 1600s.
Edit - got a good look at the label of one of these here:
http://www.kitguru.net/components/p...eadex-platinum-8-pack-edition-2000w-review/3/
Yeah, theirs is definitely not good for 120V operation. If yours is the same, you're pretty much not running this without a 240VAC circuit. In that case, I would suggest having an electrician run a circuit for a NEMA 6-20, then grab one of
these line cords, third table down.