Global temp = 22C
Room C/W = 0.005
Fan Heat Dump = 2.0W
The proposed tubing sizes and fittings we'll be investigating are:
6.35 (1/4") ID tubing with quick-fit fittings
8mm (5/16") ID tubing over 6mmID|8mmOD barbs
8mm (5/16") ID tubing with quick-fit fittings
9.6mm (3/8") ID tubing over 7.5mmID|3/8"OD barbs
9.6mm (3/8") ID tubing with quick-fit fittings
11.1mm (7/16") ID tubing stretched over 10.5mmID|1/2"OD barbs
12.7mm (1/2") ID tubing over 10.5mmID|1/2"OD barbs
The total CPU heat load is 100W. The total system heat load is 114W . We assume a fixed 14W heat dump from pump which was derived from other testing. This does in fact vary a little as we can see by the Laing graph. As flow rates decrease, so does power draw, and therefore the heat-dump as well. For simplicity we'll assume a fixed 14W heat dump for now.
The intersections all are:
6.35mm quick fit = 4.45LPM flow, 0.0795 block c/w, 0.0374 rad c/w
8mm barbed = 4.75LPM, 0.0783 block c/w, 0.0373 rad c/w
8mm quick fit = 5.6LPM, 0.0770 block c/w, 0.0369 rad c/w
9.6mm barbed = 5.7LPM, 0.0768 block c/w, 0.0369 rad c/w
9.6mm quick fit = 6.2LPM, 0.0762 block c/w, 0.0367 rad c/w
11.1mm barbed = 6.3LPM, 0.0761 block c/w, 0.0367 rad c/w
12.7mm barbed = 6.35LPM, 0.0760 block c/w, 0.0366 rad c/w
Final CPU temperature is ambient (22C) + system load (114W) * radiator C/W + CPU Load (100W) * block C/W
The final CPU temperatures work out to be:
6.35mm quick fit = 34.21C
8mm barbed = 34.08C
8mm quick fit = 33.91C
9.6mm barbed = 33.89C
9.6mm quick fit = 33.80C
11.1mm barbed = 33.79C
12.7mm barbed = 33.77C