I'm back! There's too much FUD here for me to ignore it.
Westom, do you have an answer for
any of the following questions you've been asked? Ideally, all of them?
Never answered - obvious questions:
- Why do the only 2 detailed examples of protection in the IEEE guide use plug-in protectors?
- Why does the NIST guide says plug-in protectors are "the easiest solution"?
- Why does the NIST guide say "One effective solution is to have the consumer install" a multiport plug-in protector?
- Why does the NIST guide say "Plug-in...The easiest of all for anyone to do. The only question is 'Which to choose?'"
- Why do westom's "responsible companies" make plug-in protectors?
- Why does "responsible company" SquareD says "electronic equipment may need additional protection by installing plug-in [protectors] at the point of use"?
Also, what does the NIST say about what a "proper" ground is? Please cite
with a link to the guide and a page number, not just a copy/paste. If you're going to convince us you're going to have to cite things properly.
On the subject of capacitors: Do you know the difference between a non-PFC appliance and capacitors, a passive PFC appliance and capacitors, and an Automatic PFC appliance and capacitors?
In my capacitor based examples I said APFC multiple times, an APFC takes the incoming voltage and
actively boosts it to ~380v before storing it in a capacitor. In PSUs that capacitor is rated for somewhere between 380v and 450v. I've yet to see a higher rating.
The APFC circuit can completely
ignore a surge up to that voltage point, as it will not even get through the PFC boost diode and into the capacitor until the voltage is higher than 380v. For bonus points most PSUs these days have a TVS Diode (
NOT a MOV. They serve the same function but have
very different specs) that triggers in the 400v range somewhere. That mops up a lot more surges.
It is wired across the live and neutral wires.
A passive PFC unit uses a voltage doubler and two 200v capacitors to achieve a voltage somewhere in the mid to high 300v range. Crucially the capacitors are wired in series (sort of) so each capacitor only has to deal with half the voltage. They also have a MOV or TVS Diode, wired the same way, for the same purpose: deflecting surges.
A non-PFC unit is much simpler, it just rectifies the incoming voltage to DC and stashes it in a capacitor. That capacitor is probably rated for around 200v. I have no experience with them and cannot comment on their internals.
Now like I said, I was talking about APFC computer power supplies. Let's step through what happens in a surge, shall we?
Surge begins, voltage rises and current starts to flow.
The APFC unit says "Oh ok, that's cool, I can auto-range between 90v and 264v!" and keeps on doing what it wants to do and drawing exactly as much current as it wants to.
Meanwhile the surge continues, it cannot dump all the current it wants to, so the voltage continues to rise.
At 264v (AC mind you, so ~373v DC. Familiar sounding number?) or so the APFC says "Uhh hey, we're kinda done here man" and does one or two things.
The first thing is to stop boosting the voltage, it doesn't have to. It'll still boost it in the off-peak areas, but not peak.
The second thing it may do, if the APFC voltage goes too high, is to shut down the primary switches for the PSU's DC-DC regulator.
These switches are rated at between 500v and 800v in my experience.
I checked the datasheet for
two different 600v-650v units and both suffer avalanche breakdown at 700v. At that point you have 700v going through the PSU's transformer rather than 380v, and odds are it's game over.
However, 700v is far higher than the trigger point of the TVS diode. It opens up (quickly,
a few picoseconds) and starts dumping the surge to neutral. Note that a PSU does not care what the hot-ground voltage is, only hot-neutral. The primary side of the unit (that which deals with line voltages) is isolated from ground. The entire APFC unit is, so it only cares about the difference between live and neutral.
Anyway, once the TVS diode is dumping it can flow a
huge number of amps. In a brief surge it will simply deflect it for the duration of the surge, the APFC bits never see it. Just past the TVS diode is the transient filter, which further serves to delay a brief surge.
In a longer surge the obscene current through the TVS diode will blow the fuse, no more issues.
Now please note that the above example doesn't require a ground path at all due to the way APFC PSUs are designed.
Bonus: A post occurred while I was typing.
I think I see where your confusion comes from.
That first link and its TVSS info states it requires a good ground. Because it does.
The issue they were having previous was due to bad, horribly wired, grounds. That's a major issue.
It also has absolutely nothing in common with a house that doesn't have neutral tied to ground.
Note that nowhere does it say it must be less than ten feet to anything.
Neither link says
anything about internal surge protection, either.
The first block quote is quite literally useless. I could type one up from Joe Smith that supports my points too. He has 45 years of experience.
Now I need to take my kids to school, but rest assured that I'll be back soon.