Yikes, do you mind if I ask where you are located? That looks like pretty new construction
It's indeed new construction. I'm in Saudi Arabia.
I'm surprised ground wasn't mandated.
Well, I think that's because the electricity company is grounding the main lines from the district transformer, but this is the point I want to be sure of because I measured the current from neutral to PSU chassis and it was 0A as the voltage on the chassis is 110V !!
I am still a little skeptical that this could cause all of your problems.
It's absolutely the reason, because the PSU need the 3 ground wire which left unconnected and having 110V that need to go the ground, because of the AC main input filtering capacitors.
I've operated PCs in houses with old construction that did not have a ground and I never experienced this effect. I'm no electrician but I don't believe the system should be dumping current to ground. I would suggest checking your motherboard mounting,
All other appliances that have so exposing ground to people can cause electric shocks if they are not grounded!
Like my dish washer, the internal metal area is grounded, but my electricity is not grounded, so there are 110V are left on this part and shock me every time I touch it as the machine is connected to power.
same story with the refrigerator also my espresso machine that has metal parts outside; like this one:
check all your wires for loose or frayed connections. You said it does this even with the new PSU? You might need to re-assemble the entire system outside of the case in a test bench to see if you can stop the problem.
the shocks are present even when the PSU is connected alone:
But this picture was because I wanted to measure the current from neutral to chassis and it was 0A.
It is infuriating that your distribution box has a grounding bus but it was not used. What gives with that?
Yep! The box is designed to more safer electrical installation but the building owner choose not to install grounding system because that cost them some money and most people here don't need the ground because I think the electricity company already grounded the neutral wire.
I would check into the electrical regs and if you find out the wiring is in violation of code I would report the landlord/owner to the appropriate municipal agency. If the owner/landlord won't commit to correcting the code discrepancy I would consider a law suit or at least moving. The pictures you have taken of the electrical system would be solid evidence.
I called the electricity company, they said to my that their responsibility is to ground their mains and the owner responsibility is to ground the house.
So I can't sue anyone here ! welcome to Saudi Arabia
I certainly would not jury rig a ground.
Did not understand what you mean here ! Could you explain more ?